Rick 0920
Senior Member
- Location
- Jacksonville, FL
- Occupation
- Electrical Instructor
When doing dwelling service calculations, one of the last steps has always been to increase your largest motor by 25% to accommodate for motor inrush current on the service conductors. With the change made to 220.60 where if the A/C is the smaller of the noncoincident loads, we then increase it by 25% if it is the largest motor. (which it usually is in a dwelling). If this step is done, is it still necessary to take your largest motor and increase it? It seems like we are doing it twice. The example in Annex D1(b) shows this step in the 2020 NEC even though the change is there in 220.60 for noncoincident loads.