That's a good point on NEC 220.60, I think that non coincident is being miss-applied.
Well I do not see a distinction in the NEC.
If only one of two loads can run at one time you only have to worry about the heaviest of them.
...
You don't see a distintion between Part II and Part III of Article 220?
I do not see anything in the NEC that requires me to calculate a circuit based on what is not connected to it.
Hmm, maybe not. But very often a room full of lights is not connected to its circuit, yet I bet we add the load.
I will allow though that the SPDT or DPDT is different situation.
Those were my thoughts as well, any switch disconnects the equipment from the circuit but there seems to me to be a difference with a selector type switch.
As much as I agree the situation the OP describes is not what the NEC intends I do not see a safety issue.
Obviously, but what about the required 2 SABC's?
I believe they're trying to designate the refrigerator as one of the kitchen circuits, and the microwave as the other. In this case, they're switching between the two with one home run.
There need to be two or more 20 amp branch-circuits. Can't get around that requirement. If only one 'home run', it can be a 12/3 (multi-wire) circuit, fed from two handle-tied breaker poles. Or it can be two 12/2 circuits, fed from two breaker poles. But it can't be a single circuit to feed the common of a double-throw switch.Guess they figure that NEC 210.11 is satisfied with the switching.