If a 7 dwelling unit apartment building has:
1 counter-top double burner range, 1800VA (which is greater than 1750VA), 120 volts, in each Unit and
1 Oven 4000VA, 120/240 volts, in each Unit.
What would be the total calculated VA, using 220.55 & 220.61, for these cooking appliances on the neutral conductor?
I am afraid that if I use table 220.55 to calculated the ungrounded load and then apply a demand of 70% for the neutral, I would under
rate my neutral because the ranges are 120 volts. Is 220.55 only for cooking Appliances that are rated 120/240 volts where neutral
conductor load is concerned?
Thanks