Hey guys,
I'm looking at section 220.82 in the 2008 NEC, the optional calculation for a dwelling unit. In order to be able to use this section, the total connected load has to be served by a single 120/208 or 120/240V set of 3 wire service or feeder conductors, with an ampacity of 100 amps or greater.
My 2 questions are:
1. this section is based on total connected load, and not demand load, is that correct?
2. If my demand load is 78 amps, but my connected load is 102 amps... I could use #4 AWG feeder wiring, which is rated for 85 amps, based on demand load. But am I allowed to use this section? Since the total connected load is 102 amps which would require #2 AWG feeder wiring. But i would only be specifying #4 wire based on demand load.
I'm looking at section 220.82 in the 2008 NEC, the optional calculation for a dwelling unit. In order to be able to use this section, the total connected load has to be served by a single 120/208 or 120/240V set of 3 wire service or feeder conductors, with an ampacity of 100 amps or greater.
My 2 questions are:
1. this section is based on total connected load, and not demand load, is that correct?
2. If my demand load is 78 amps, but my connected load is 102 amps... I could use #4 AWG feeder wiring, which is rated for 85 amps, based on demand load. But am I allowed to use this section? Since the total connected load is 102 amps which would require #2 AWG feeder wiring. But i would only be specifying #4 wire based on demand load.