Correct. And I would even say you could use #4 according to 310.12..... would this be correct, or wrong?
Correct. And I would even say you could use #4 according to 310.12..... would this be correct, or wrong?
ah. and what about the fusing? let's say 220.82 brings my connected load of 60 amps down to 41 amps. Can i use a 45 amp breaker / set of fuses? or does the 100 amp wire have to be protected at 100 amps (let's assume i'm using #3 wire)?Correct. And I would even say you could use #4 according to 310.12.
ah. and what about the fusing? let's say 220.82 brings my connected load of 60 amps down to 41 amps. Can i use a 45 amp breaker / set of fuses? or does the 100 amp wire have to be protected at 100 amps (let's assume i'm using #3 wire)?
Yeah I got it now. I find this section a little 'off', but I got it. Understood about the #3's not being able to connect to the 45 amp breaker. Was just curious about the numbers aside from the physical limitations. Thanks for the help!I suppose there's no code rule against that, if the breaker is not a service disconnect or a detached building disconnect. (e.g. it's in a multi dwelling building). However you won't be able to land #3 on that 45A breaker that you special ordered inadvisadly. And, what would be the point?
As Dennis pointed out in post #8, it appears that the language in 220.82 would preclude its use with #4 conductors.Correct. And I would even say you could use #4 according to 310.12.
As Dennis pointed out in post #8, it appears that the language in 220.82 would preclude its use with #4 conductors.
The wording in 220.82 doesn't say anything about "whatever 310 says you can use for 100A."In my opinion the wording in 220.82 should be read as whatever 310 says you can use for 100A. Therefore, see 310.12.
The wording in 220.82 doesn't say anything about "whatever 310 says you can use for 100A."
It says "service or feeder conductors with an ampacity of 100 or greater."
According to Art 310, #4 conductors do not have an ampacity of 100 or greater.
Three points:
First, 310.15(A) begins: "Ampacities for conductors rated 0 volts to 2000 volts shall be as specified in the Ampacity Table 310.16 through Table 310.21, as modified by 310.15 (A) through (F) and 310.12." (Emphasis mine.) Pretty direct contradiction of your last sentence.
Second, "whatever 310 says you can use for xxA" is as good as any guidance you'll find in the NEC on how to determine what 'ampacity' is when other articles refer to it. The article 100 definition of ampacity really sheds no light on the contradiction between the way it is used in 310.12 vs everywhere else I've noticed.
Finally, when the language of 310.12 (formerly 310.15(A)(7)) was revised a few cycles ago, there clearly was no intent to change the application of 220.82.
No it doesn't.
...
If 310.12 said that the ampacity of #4 was 100A, there would be no issue.
...
There is (and always has been) a disconnect between 220.82 which requires a service/feeder conductor ampacity of 100A or greater and 310.12 which permits a service/feeder ampacity which is lower than 100A.
If you can't address that point more substantively then I really need not say much more. What I quoted says that 310.12 modifies the ampacity of conductors. That's what it plainly says. Which makes everything else you said fairly irrelevant.
Before the old 310.15(B)(7) was modified with it's inconsistent use of 'ampacity' then there were no contradictions. Again, see 310.15(A) in the 2020 NEC.
... If you could point to the language in either of those sections that tells you the ampacity of the #4 conductors has increased to 100A, you would have a point. But no such language exists. You're reading what you want the sections to say rather the what they actually say.
I don't need to cite language in 310.12 because 310.15(A) explicitly encompasses 310.12.
Once again, the text of 310.12 doesn't say anything about modifying the ampacity of conductors. Stop ignoring what 310.12 says.Once again, 310.15(A) says that 310.12 modifies the ampacity of conductors. Stop ignoring that.
310.12(A): For a service rated 100 amperes through 400 amperes, the service conductors supplying the entire load..shall be permitted to have an ampacity not less than 83 percent of the service rating.
...
310.15(A): There is nothing in the rest of 310.15(A) that modifies the ampacity of conductors. (0-1)
310.15(B): Ampacities...shall be corrected. This actually modifies conductor ampacity. (1-1) - batting .500
310.15(C): Ampacities...shall be be reduced. Two in a row modifying ampacity. (2-1)
310.15(D): Nothing that modifies the ampacity of conductors (2-2) - back to even
310.15(E): Nothing that modifies the ampacity of conductors (2-3) - sub .500
310.15(F): Nothing that modifies the ampacity of conductors (2-4)
310.12: Nothing that modifies the ampacity of conductors (2-5)
How is it possible that of all of the sections that 310.15(A) says will "modify the ampacity of conductor," only two actually provide direction to do so?
Could it be that the language "as modified by 310.15(A) through (F) and 310.12" isn't an absolute direction that those sections will change the ampacity of a conductor, since most of the listed sections don't provide any direction on modifying the ampacity of a conductor?
Since you are so caught up in the language in 310.15(A) ("as modified by 310.15(A) through (F) and 310.12") that it causing you to ignore the plain language in 310.12
Maybe the Code writers themselves could provide some insight, since they revised the language of 310.15(B)(7) in the 2017 Code ...
(7) 120/240 Volt, Single-Phase Dwelling Services and Feeders. For service
and feeder conductors of 120/240-volt, single-phase, individual dwelling unit
one-family, two-family, and multifamily service ratings from 100 through 400
amperes, an adjustment factor of 0.83 of the service ampere rating shall be
permitted to be used to determine the size of the ungrounded conductors.