I need to do a service upgrade for a house from 100A to 200A. I have done this before..4/0 ALU....bla bla bla
However, I have never done one for a house that has (2) meters. The customer is requesting to replace both meters and both panels from 100A to 200A.
My question is the following:
1)Can I use 4/0 AL for my SE cable to power both panels? or do I need to upsize the wire?
2)Do the meters get wire in parallel?
3)Do I need to do individual ground rod to each new panel?
Any help or suggestion will be well received.
Thanks

Jason