358.10(B) permits it with limitations, however I wouldn't do it. A few years later all you will find is a little rust.j rae said:Can you run emt under ground with compresion couplings?? Can you use an eirkson fitting underground????
ultramegabob said:what possible reason would you want to? pvc is easier to work with, costs less, and would last much longer....
mdshunk said:There was a time where the sweep and riser for underground services was done in EMT in my area. This has been a fairly steady source of service calls, since they rot off at ground level and what's left underground resembles rusty flakes. I don't even like EMT outdoors, much less underground. There's just better options, and the most popular better option is cheaper.
j rae said:Can you run emt under ground with compresion couplings?? Can you use an eirkson fitting underground????
358.10(B) permits it with limitations
In general, galvanized steel electrical metallic tubing in contact with soil requires supplementary corrosion protection.
They are just as water tight as is a threaded coupling.russ said:eirksons are not listed for underground use.
They are concrete tight but not water tight.
220/221 said:Dear God, tell me it's April fools day.
I have just lost a little more respect for the fine folks who write the NEC.
EMT underground....nice. Don't get me wrong. I have SEEN it, I just assumed some handyman who didn't know shirt from shinola installed it.
russ said:eirksons are not listed for underground use.
They are concrete tight but not water tight.
My guess is that the OP had two unrelated questions.HighWirey said:Just a neophyte here. Why would you use an erickson coupling with EMT?