E-Stop On Residential Generator

Status
Not open for further replies.

NorthwestPV

Member
Location
Oregon, US
We are installing a 350KW, 480V generator in a residence. I was reviewing the start up check list. One of the checkboxes is for the emergency stop switch installed. Is this switch required?
 
That's probably more of a manufacturer question if the generator is installed to code. Disconnects, clearances, etc.

350kw 480v for a residence?!? That's huge Is this for a multi family place, or the bat cave?

Sent from my SM-G950U using Tapatalk
 
Seriously though, that must be a huge house. Why go with 480 volt?

And 702 doesn't require any type of emergency stop switch for an optional standby system. So you wouldn't be violating any codes by skipping it. I would say that if the remote switch is listed for use wth your generator than its not an issue.

Sent from my SM-G950U using Tapatalk
 
We are installing a 350KW, 480V generator in a residence. I was reviewing the start up check list. One of the checkboxes is for the emergency stop switch installed. Is this switch required?

It may be for the fireman. I would check AHJ if needed by local code.
 
We are installing a 350KW, 480V generator in a residence. I was reviewing the start up check list. One of the checkboxes is for the emergency stop switch installed. Is this switch required?

NEC 2017 445.18 (B) (2)
This is new in 2017
 
NEC 2017 445.18 (B) (2)
This is new in 2017
Missed that cause i was looking at 14 when he first posted.

The last paragraph of B(2) seems like that remote e stop he's asking about will be required on a gen of his size.

Gens over 15kw...require additional shutdown means located outside equipment room or generator enclosure.

Sent from my SM-G950U using Tapatalk
 
Missed that cause i was looking at 14 when he first posted.

The last paragraph of B(2) seems like that remote e stop he's asking about will be required on a gen of his size.

Gens over 15kw...require additional shutdown means located outside equipment room or generator enclosure.

Sent from my SM-G950U using Tapatalk
On a machine of that rating I would have one anyway whether or not the code requires i.
 