We are installing a 350KW, 480V generator in a residence. I was reviewing the start up check list. One of the checkboxes is for the emergency stop switch installed. Is this switch required?
We are installing a 350KW, 480V generator in a residence.
350kw 480v for a residence?!? That's huge Is this for a multi family place, or the bat cave?
Holy Guacamole, Batman! :blink:Bat Cave, and it's not a full time home
We are installing a 350KW, 480V generator in a residence. I was reviewing the start up check list. One of the checkboxes is for the emergency stop switch installed. Is this switch required?
We are installing a 350KW, 480V generator in a residence. I was reviewing the start up check list. One of the checkboxes is for the emergency stop switch installed. Is this switch required?
Missed that cause i was looking at 14 when he first posted.NEC 2017 445.18 (B) (2)
This is new in 2017
On a machine of that rating I would have one anyway whether or not the code requires i.Missed that cause i was looking at 14 when he first posted.
The last paragraph of B(2) seems like that remote e stop he's asking about will be required on a gen of his size.
Gens over 15kw...require additional shutdown means located outside equipment room or generator enclosure.