Thanks for the replies guys.
The application is for heaters. You had mentioned 30mA and 100mA, how about the time setting/duration?
These are for standard off the shelf single phase units and they come with a fixed setting and no adjustable time delay.
As it happens, I'm currently working on a quotation for a heater panel, quite a big one, it's 3-phase, rated at 930kW total, and made up of four sections. Each of the four will have adjustable earth fault protection and the customer specification calls for a range of 100mA to 3A and a time delay of zero to ten seconds.
I'm proposing units we've used before for the same customer. It comprises a three phase system and a core balance current transformer and a current sensor.
Main specifications:
Earth fault ranges: 5-100mA, 50mA-1A, 0.5-10A
Hysteresis: Fixed at 5% of set value (other values on request)
Tripping delay: Adjustable 0.1-10secs
In accordance with: EN61000-6-1: 2007 EN61000-6-3: 2007 EN61010-1: 2002
Conforms to: IEC44-1, IEC185, BS7676