More or less just wondering if others give this any thought? I mean, there is a whole section on this site, dedicated to just this, in which, IMO, could mean it's hard to understand, though the concepts are simple, and I believe it's because you are doing TWO things with that conductor system, and that should be more clear!
When I look at a electrical system for the first time, I want to know 3 things
What is the relationship of the distribution transformer (or generation source) to a grounding electrode system (GES)?
What is the relationship of exposed-conductive-parts and any equipment grounding conductors to a GES?
Which conductors if any are current carrying and grounded / neutral and what conductor provides the equipment grounding conductor / protective earth function?
To me the
IEC terminology for this is very helpful, and I can answer my 3 basic questions in a simple way
In IEC terms I start at the secondary of a transformer (or generation source):
The First Letter (I or T) indicates the relationship of the distribution transformer to 'ground'.
T = direct connection of one point to earth.
I = all live parts isolated from earth, or one point connected to earth via a high impedance.
The second letter indicates the relationship of all exposed-conductive-parts and any equipment grounding conductors to a grounding electrode system.
T = direct electrical connection to a grounding electrode system independent of any other grounding electrode system.
N = direct electrical connection of a point on the transformer (neutral or phase etc) to the grounding electrode system and thus the equipment grounding conductors.
Subsequent letter with a dash - (if any) and describe the arrangement of neutral and equipment grounding conductor
S = Grounds and neutral (or grounded phase) are run separately all the way from the distribution transformer.
C = neutral (or grounded phase conductor) and equipment grounding provided by the same conductor
So a multi grounded neutral (MGN) utility system is TN-C and after the service disconnect we use a TN-S.
We can describe the entire system as TN-C-S;
T) Because at the secondary we have a direct connection of one point to a GES;
N) We have direct electrical connection of the neutral point or a line conductor to the GES and thus the equipment grounding conductors.
Then for the conductors
-C The utility neutral is combined with the equipment grounding conductor until the service disconnect.
-S After the service disconnect they are separate
If it was a SDS in a building say a 208 transformer off a 480V system the 208 system would be TN-S in IEC terms.