crossman gary
Senior Member
I did the following experiment this afternoon just to prove to myself what was the real deal about the voltage drops around a driven electrode.
I had assumed that the low resistance of the soil in my area would have prevented much of a voltage drop in the "earth shells" around the electrode - and stated as much in the "construction trailer - ground rod" thread located here:
http://forums.mikeholt.com/showthread.php?t=114269
Here is a photo and a diagram of my results based on the following: My power source was 50 volts 60Hz AC and this was pushing 6 amps through the hot wire to the 5 foot deep pipe into the earth. I didn't use 120 volts because it would have tripped the OPCD of my supply as evidenced in previous experiments which are documented elsewhere on the forum.
Soil conditions were moist, must have had some rain in the past few days as there was a bit of standing water in the ditches in the area. (I was out of state last week so I don't know if it rained but it must have)
If we want to consider 120 volts instead of the 50 volts, we can just multiply the voltage drops by the ratio 120/50.
Note: The pipe driven at 1 foot from the electrode was put in after I took the photo.
I was very surprised to see such a high voltage drop around the pipe! I was almost in disbelief.... I was using a digital meter, so then I did the same measurements with a Simpson. Same results. Wow. So in my head I am thinking this has to be some kind of "ghost voltage/capacitive something" due to the high impedance of the meters.
So I took a small 24 volt indicator lamp, attached some leads, and put it across the electrode to the 1 foot pipe. It lights up brightly! Wow again.
I carefully disconnected the hot wire from the electrode and there was a discernible spark. I measured the voltage from the hot wire to the electrode and of course it measured 50 volts.
So okay, well, the test pipes are driven in 1 foot. What if we wanted to see what would happen if a person walked barefoot in the area? We took the digital meter, held one lead on the electrode, and then simply placed the other lead down in the grass... bingo... just about the same voltage readings as the test pipes. Wow again.
Anyway, there ya go. Nothing like actually performing the experiment to make a believer out of you (me).
Conclusion: In the experiment with the hot wire detached from the electrode, there was a 50 volt shock potential. With the electrode attached, the shock potential was lessened a little, 33 volts at 1 foot from the electrode, 41 volts at 2 feet away, and increasing.
While an electrode most likely will lower the shock potential from an energized object, it certainly will not nullify the entire potential. The EGC is absolutely the most important item for safety ( I always believed this, and would never rely solely on the electrode. I admit that I believed the electrode would have done a lot more to eliminate the potentials in the area.)
Moral:
1) Follow the Code!
2) This was a great learning experience.
3) Crow doesn't taste all that bad really.
I had assumed that the low resistance of the soil in my area would have prevented much of a voltage drop in the "earth shells" around the electrode - and stated as much in the "construction trailer - ground rod" thread located here:
http://forums.mikeholt.com/showthread.php?t=114269
Here is a photo and a diagram of my results based on the following: My power source was 50 volts 60Hz AC and this was pushing 6 amps through the hot wire to the 5 foot deep pipe into the earth. I didn't use 120 volts because it would have tripped the OPCD of my supply as evidenced in previous experiments which are documented elsewhere on the forum.
Soil conditions were moist, must have had some rain in the past few days as there was a bit of standing water in the ditches in the area. (I was out of state last week so I don't know if it rained but it must have)
If we want to consider 120 volts instead of the 50 volts, we can just multiply the voltage drops by the ratio 120/50.
Note: The pipe driven at 1 foot from the electrode was put in after I took the photo.
I was very surprised to see such a high voltage drop around the pipe! I was almost in disbelief.... I was using a digital meter, so then I did the same measurements with a Simpson. Same results. Wow. So in my head I am thinking this has to be some kind of "ghost voltage/capacitive something" due to the high impedance of the meters.
So I took a small 24 volt indicator lamp, attached some leads, and put it across the electrode to the 1 foot pipe. It lights up brightly! Wow again.
I carefully disconnected the hot wire from the electrode and there was a discernible spark. I measured the voltage from the hot wire to the electrode and of course it measured 50 volts.
So okay, well, the test pipes are driven in 1 foot. What if we wanted to see what would happen if a person walked barefoot in the area? We took the digital meter, held one lead on the electrode, and then simply placed the other lead down in the grass... bingo... just about the same voltage readings as the test pipes. Wow again.
Anyway, there ya go. Nothing like actually performing the experiment to make a believer out of you (me).
Conclusion: In the experiment with the hot wire detached from the electrode, there was a 50 volt shock potential. With the electrode attached, the shock potential was lessened a little, 33 volts at 1 foot from the electrode, 41 volts at 2 feet away, and increasing.
While an electrode most likely will lower the shock potential from an energized object, it certainly will not nullify the entire potential. The EGC is absolutely the most important item for safety ( I always believed this, and would never rely solely on the electrode. I admit that I believed the electrode would have done a lot more to eliminate the potentials in the area.)
Moral:
1) Follow the Code!
2) This was a great learning experience.
3) Crow doesn't taste all that bad really.