Been doing a lot of electrical work for a local hotel recently. I've noticed that quite a few of their PTAC units are 7k BTU, and come with 6-15 plugs, and are rated for 15A circuits. ofc they are on 20A circuits, above what the mfg requires (MCA 15A, MOCP 15A). 6-20Rs accept 6-15 plugs.
Is/was there an exception in older codes where this install was legal? There is one unit per circuit.
Eqpt is roughly 20 years old, place was wired in the late 60s early 70s. Quite a few of the plugs and/or receptacles have burned up, tho I believe that's more to do with them being not completely plugged in or mfg defect than the 20A breakers.
Is/was there an exception in older codes where this install was legal? There is one unit per circuit.
Eqpt is roughly 20 years old, place was wired in the late 60s early 70s. Quite a few of the plugs and/or receptacles have burned up, tho I believe that's more to do with them being not completely plugged in or mfg defect than the 20A breakers.