This company has many radio tower sites, and most are using the 9170+ UPS. Single phase 240/120 for emergency and for filtering the POCO power.
I was asked to check power quality from the utility to the UPS at this one site. Utility power only, no genset. Control house is climate controlled.
They were using only one module on test day. At this site, they have changed batteries and changed modules. Sometime the module runs for an hour, sometimes a day. Move the modules to another tower site and no problem with the module.
With only one module running and the risk of an outage to the tower, testing on the load side was limited. PMI voltage recorders were set in the meter socket for a week, and no PQ issue was seen. Thermal imaging on the UPS tower has been done
Next week they plan to move this site to bypass so more UPS load testing can be done.
This is a rare problem for this company, but they have experienced it before, and the cure was total removal and replacement with a DC plant.
There wasn’t information on alarms. The communications group receives a notification that the site is down and when they show up, the module is offline.
We can resistively load the UPS and have meters to see the sine wave.
What test can be done to isolate and correct this problem?
Thanks,
I was asked to check power quality from the utility to the UPS at this one site. Utility power only, no genset. Control house is climate controlled.
They were using only one module on test day. At this site, they have changed batteries and changed modules. Sometime the module runs for an hour, sometimes a day. Move the modules to another tower site and no problem with the module.
With only one module running and the risk of an outage to the tower, testing on the load side was limited. PMI voltage recorders were set in the meter socket for a week, and no PQ issue was seen. Thermal imaging on the UPS tower has been done
Next week they plan to move this site to bypass so more UPS load testing can be done.
This is a rare problem for this company, but they have experienced it before, and the cure was total removal and replacement with a DC plant.
There wasn’t information on alarms. The communications group receives a notification that the site is down and when they show up, the module is offline.
We can resistively load the UPS and have meters to see the sine wave.
What test can be done to isolate and correct this problem?
Thanks,