Davids1973
Member
- Location
- Florida
- Occupation
- Electrician
Got a service call today from a customer that said they had multiple Breakers tripped in their panel. After arriving site I checked the main disconnect outside and they had appropriate voltage . I went inside the residence and checked the voltage at the panel inside and all was appropriate. All the art fault ground fault breakers on the B phase were tripped. I reset them all and they held. The homeowner told me this isn't the first time that this has happened that is a regular occurrence. I had a hunch it was a critter issue. I went out to the meter main combo and cut the meter tags and pulled the meter. As suspected there was a frog bridging the gap between the can and the B phase. After the critter removal all was good. Just wanted to out that out there for anybody running across the same situation.