Here's the story behind the issue.The State of TN has sent out a notice to inspectors alerting them that the Eaton ACD are not to be used for EV, PV or RESISTIVE HEATING loads per manufacturer instructions (attached)
Allegedly, there have been fires involving these pullout units on resistive heating loads.
Has anyone experienced this ??
(Expanded from Eaton Publication IL007001EN )
This ACD is not intended for uses on electric vehicle (EV) charging, photovoltaic, and resistive heating applications. Eaton’s recommended disconnect switch for these applications is DPB222R.
youtube.com/watch?si=L0AdnG5eiMfmMMZX&v=WiqAO7HptYw&feature=youtu.be
As a home inspector, I sometimes find these pullout-style disconnects not fully seated. That'll overheat one in a hurry, particularly under a constant, heavy load.
I don't commonly encounter a pullout-style ACD in an attic, but the homebuilder Meritage uses them. In most homes there is no 220V disconnect in the attic, it's just a 120V switch for the low-current stuff in the air hander.