EATON GFCI SGF15-M
lpfam111
Houston
I am installing an EATON SGF15-M gfci receptacle under the sink. I am trying to make it a split circuit but I can’t find the “break off” tab. Does this model receptacle not have a break off tab?
Dennis Alwon
Chapel Hill, NC
Electrical Contractor
Remember there is a line and load so there is no way to get 2 circuits from one Gfci. Install a 2 gang box and use 2 gfci's
ramsy
LA basin, CA
Push button resets are not allowed under sinks with cabinet doors, or behind cabinet doors at all.
See "Readily Accessible" in new work code 210.8, and Replacement Code 406.4(D)
Dennis Alwon
Chapel Hill, NC
Yes they need to be readily accessible but it definitely arguable whether under a sink is readily accessible. IMO, if the receptacle is close to the front of the cabinet then it is considered readily accessible.
I don't see anything that states it cannot be behind a door.
lpfam111
Houston
There is a 2 gang box with 2 romex feeds. One is black red white gnd. That’s the one wired to the switch. The other romex is just black whit gnd but when I wire that to a second gfci it trips the breaker. The black red white works fine and operates by the switch.
ramsy
LA basin, CA
I like your interpretation, but the senior planner who instructs our local IAEI tells inspectors to red tag it, forcing the reset placement elsewhere.
I believe he uses this to force kitchen remodels to upgrade the electrical service when older panels won't except a GFCI breaker.
Dennis Alwon
Chapel Hill, NC
You do realize that we are not allowed to help with diy projects. I know you are an ee but unless you are qualified as an electrician then we cannot help.