are EBU's required in electrical closets? this is not a main electrical room? any thoughts would be appreciated
thank you(2015) IBC 1008.3.3
In the event of power supply failure, an emergency electrical system shall automatically illuminate all of the following areas:
1. Electrical equipment rooms
2. Fire command centers
3. Fire pump rooms
4. Generator rooms
5. Public restrooms with an area greater than 300 square feet
Take a look at NFPA 101 (Life Safety Code) for more information on emergency lighting requirements. Section 7.9.thank you