EC&M Grounding & Bonding
tom baker said:
A switch is not part of the EGC path, a receptacle is.
a lot of metallic items are not part of the grounding path, but are required to be bonded......~RJ~
I think Tom is referring to the self grounding receptacle yoke like I did on post #10
The receptacle's yoke has to carry the fault current but the switch strap doesn't. Well... I guess technically it does but it is not the fault current of an appliance.
reading 404.9 B we have three exceptions that are pertinent to OP
ex #1, we replace a switch in ancient non-egc , it's either non metallic yoke of GFI protected
ex#2 states all four (4) need to be met...for manufactured homes cheesy 'switch in a box' garbage
ex#3 is talking more of the same & kicks us back to 300.15E>>>
(E) Integral Enclosure. A wiring device with integral enclo‐
sure identified for the use
All of this is the manufactured home industries influence to beat stick built per sq ft, because they use substandard materials they lobby cmp's to create codes as well as exceptions to codes for Ed
we don't wire like this, so anything we run an egc to, is supposed to carry the 'fault current' , be it a direct or indirect path back to source
~RJ~
What do you think? I always thought you needed self grounding device unless it had metal to metal contact. According to the article you only need that for receptacles.
RJ can you explain how those exceptions have anything to do with Dennis' question from the OP (quoted above)?
The question is can the switch be grounded by only the two metal mounting screws without the use a self-grounding device. The answer is yes, Mike's graphic contains the applicable code section.
I thought i just posted the 'explanation' infinity
the pix merely states the yoke does not need to press up against the metal box, the two 6-32 screws will do
ergo and egc is achieved, albeit mechanically connected is somewhat suspect
in no case does this imply an egc is not needed
~RJ~
~RJ~
If it was not needed, would the code stated otherwise required one like it does for receptacles without the self grounding.
The particular code OP pix is allowing a switch w/out self grounding yoke to serve as an egc via metal box, if there were an egc within said box , and if i'm reading you right, the Q would be if it were also required to be made to the switch as well
~RJ~
~RJ~
Good question.
IMO, no.
I will look in the book tonight abd see if I can change my answer.
I'd still say no, because the EGC connection option for a receptacle is to the receptacle, not the box.
~RJ~
I agree with the others no bonding jumper is required.
I read 404.9(b)(1) again and the connection of EGC to the switch is not required even with metallic conduit and an EGC.
Correct, the wire type EGC can connect directly to the metal box. The switch connects to the box with the 6/32 screws, job done.