A switch is not part of the EGC path, a receptacle is.
I have never seen the device mounting screws in plastic but the plate screws being plastic was enough to satisfy the inspections.There were nm 6/32 screws available from Leviton
which would validate grounding or isolating it w/nylon screws .......~RJ~It would be a rare case where the switch shorts to the yolk but I have seen it happen.
a lot of metallic items are not part of the grounding path, but are required to be bonded......~RJ~A switch is not part of the EGC path, a receptacle is.
a lot of metallic items are not part of the grounding path, but are required to be bonded......~RJ~tom baker said:
A switch is not part of the EGC path, a receptacle is.
reading 404.9 B we have three exceptions that are pertinent to OPa lot of metallic items are not part of the grounding path, but are required to be bonded......~RJ~
I think Tom is referring to the self grounding receptacle yoke like I did on post #10
The receptacle's yoke has to carry the fault current but the switch strap doesn't. Well... I guess technically it does but it is not the fault current of an appliance.
What do you think? I always thought you needed self grounding device unless it had metal to metal contact. According to the article you only need that for receptacles.
RJ can you explain how those exceptions have anything to do with Dennis' question from the OP (quoted above)?reading 404.9 B we have three exceptions that are pertinent to OP
I thought i just posted the 'explanation' infinityRJ can you explain how those exceptions have anything to do with Dennis' question from the OP (quoted above)?
The question is can the switch be grounded by only the two metal mounting screws without the use a self-grounding device. The answer is yes, Mike's graphic contains the applicable code section.
If it was not needed, would the code stated otherwise required one like it does for receptacles without the self grounding.I thought i just posted the 'explanation' infinity
the pix merely states the yoke does not need to press up against the metal box, the two 6-32 screws will do
ergo and egc is achieved, albeit mechanically connected is somewhat suspect
in no case does this imply an egc is not needed
~RJ~
The particular code OP pix is allowing a switch w/out self grounding yoke to serve as an egc via metal box, if there were an egc within said box , and if i'm reading you right, the Q would be if it were also required to be made to the switch as wellIf it was not needed, would the code stated otherwise required one like it does for receptacles without the self grounding.
Good question.The particular code OP pix is allowing a switch w/out self grounding yoke to serve as an egc via metal box, if there were an egc within said box , and if i'm reading you right, the Q would be if it were also required to be made to the switch as well
~RJ~
I'd still say no, because the EGC connection option for a receptacle is to the receptacle, not the box.The particular code OP pix is allowing a switch w/out self grounding yoke to serve as an egc via metal box, if there were an egc within said box , and if i'm reading you right, the Q would be if it were also required to be made to the switch as well
I agree with the others no bonding jumper is required.The particular code OP pix is allowing a switch w/out self grounding yoke to serve as an egc via metal box, if there were an egc within said box , and if i'm reading you right, the Q would be if it were also required to be made to the switch as well
~RJ~
Correct, the wire type EGC can connect directly to the metal box. The switch connects to the box with the 6/32 screws, job done.I read 404.9(b)(1) again and the connection of EGC to the switch is not required even with metallic conduit and an EGC.