That's remarkable.
I have never seen a newly installed motor get megged without evidence of a problem. In fact, I'm pretty comfortable stating that most equipment OEM's would request that you not meg the motors on their machine unless they request it because there's a problem.
I have hired people to test a motor for me (I don't own a megger as I don't need one often enough to justify hauling it around with me) when there is an obvious problem but a brand new motor that hasn't even been energized on site? No thanks. I will take my chances with the motor manufacturer's quality control. I know they're not perfect. In fact, I JUST authorized a customer to get a motor rewound when it shorted to ground after about 2 hours of operation. Haven't see a report so I don't the nature of the failure but since it ran for two hours on site plus a few minutes at my vendor's facility during pump testing, I'd guess a megger probably wouldn't have spotted a problem unless you got the motor good and hot first.
Quotes from Baldor OIM Manual:
"Minimum resistance of motor winding insulation is 5 Meg ohms or the calculated minimum, which ever is
greater. Minimum resistance is calculated as follows: Rm = kV + 1
where: (Rm is minimum resistance to ground in Meg−Ohms and
kV is rated nameplate voltage defined as Kilo−Volts.)
Example: For a 480VAC rated motor Rm =1.48 meg−ohms (use 5 M).
For a 4160VAC rated motor Rm = 5.16 meg−ohms."
Storage:
"3. Measure and record the resistance of the winding insulation (dielectric withstand) every 30 days of
storage.
a. If motor insulation resistance decreases below the minimum resistance, contact your Baldor
District office."
Removal from Storage:
"2. Measure and record the electrical resistance of the winding insulation resistance meter at the time of
removal from storage. The insulation resistance must not be less than 50% from the initial reading
recorded when the motor was placed into storage. A decrease in resistance indicates moisture in the
windings and necessitates electrical or mechanical drying before the motor can be placed into
service. If resistance is low, contact your Baldor District office."
Installation:
"First Time Start Up......
2. If motor has been in storage or idle for some time, check winding insulation integrity."
Operation and Maintenance:
"General Inspection Inspect the motor at regular intervals, approximately every 500 hours of operation or every 3
months, whichever occurs first. Keep the motor clean and the ventilation openings clear. The following
steps should be performed at each inspection:
........
2. Perform a dielectric with stand test periodically to ensure that the integrity of the winding insulation
has been maintained. Record the readings. Immediately investigate any significant decrease in
insulation resistance."