Or design the motors for the application. Make the rotor characteristics suit the requirements.
If it were almost any other industry, that would would be the case. But for transportation tunnels, if the fans don't work, the tunnel is closed. So they want standard standard standard motors that can be purchased anywhere in an emergency.
Like I said, there is a LOT that goes into the decision making process that is not normal, everything is approached as a "belt and suspenders" process. I used soft starters on a big tunnel project in NY State once, lucky for me we were not the first to propose it, otherwise it would have been a nightmare. But to give you an idea, the soft starters had to be rated to deliver locked rotor current for 60 seconds, then they had to have bypass starters cable of across-the-line emergency starting, then of course the reversing contactors, then the DC injection brake. I think those were 400HP, but by the time we got done with everything, each fan controller was in an MCC style cabinet that was 8ft. wide.
The big issue that came up was the across-the-line bypass capability, because if there was a power failure, the backup generators would be incapable of starting enough of the fans simultaneously to avoid creating the wind tunnel effect if there were to be a crash in the tunnel WHILE the generators were on-line. The solution, larger generators and then the space, fuel storage, ventilation etc. that came with that, was too costly. So they settled on acceptance of it being statistically unlikely that there would be a crash AND a loss of utility power for very long at the same time. When Super Storm Sandy hit, I thought about that exact situation at that tunnel ...
It occurs to me now that with this being a TRAIN tunnel, the rules might be slightly less stringent because the tunnel is not occupied all the time, like a highway tunnel is. Plus each car is potentially its own incendiary bomb, whereas a train, not so much. So it might very well be that these are custom motors and starting them X-Line is fine.