I am reviewing plans for a floating marina project and need some clarification. The drawings provide a chart for the power pedestal branch circuit calculations that seems to use "effective current" to size overcurrent protection. To be brief, an example single phase 120/240v circuit has a load of 270 amps (9 x 30a receptacles). After the adjustments from NEC 555.12 (80% load factor & 90% meter factor) I arrive at 194.4 amps. The chart lists an effective current of 108 amps and a 125 amp circuit breaker. I am questioning the effective current. Is the value correct? And should that be used here?