I need to amend my stance a bit. While this bit of code may be difficult or even impossible to enforce, I want to distinguish 'how hard it is to enforce' from 'how valid or important is it'. I believe that these code sections address an important issue. I believe that these code sections would be improved by having specific performance guidelines, however at some point one needs to trust human judgement.
I believe that this comes down to a judgement call by the EC. I don't see how an inspector could enforce any particular values of trip time, conductor damage, or elevated voltage in materials bonded to the EGC, but I believe that it would be entirely reasonable for an inspector to ask 'What happens if there is a short circuit on this circuit? How quickly do you expect the breaker to open? Do you expect any damage?' I believe that lack of even considering this issue would be grounds for a red tag, just like not doing a load calculation; but that with the necessary calculations if the EC simply says 'I conclude that its good enough.' then I don't see how the inspector could fail the installation.
iwire brought up the example of speed limits. Massachusetts, like many other states, has a 'Basic Speed Rule'
http://www.mass.gov/legis/laws/mgl/90-17.htm
http://www.mass.gov/rmv/dmanual/chapter4.pdf
In a nutshell, no matter what the posted speed limit is, you are speeding if you are going too fast. And I'm sure that we can come up with situations in which we would all agree that a reasonable and prudent speed is far less than the posted speed limit, but there are likely many grey areas. Rather difficult for a cop to enforce
yet important because the law _cannot_ describe every single possible situation, and at some level has to trust people simply to be reasonable. At a practical level, this sort of law would never be enforced by a speeding ticket, but instead would come up in a lawsuit and only if there were an actual accident.
For what its worth, marketing literature that I've seen makes the claim that the armor and bonding strip of AC cable has lower resistance than the required equipment grounding conductor if the EGC were wire sized by 250.122.
-Jon