EGC as GEC seems to be a hot topic that has been discussed in great depth already on this forum; unfortunately, I have not seen a definitive answer to my specific question so I thought I would spark a continued discussion now.
We use the same vendor for compressors on all of our sites and provide the same single line for each installation. The compressor MCC has a 5kVA 480/120V step down transformer to provide control power and 120VAC auxiliary power. Dozens of other sites have received inspector approvals, but this new site we're building is receiving push-back because we do not detail a connection back to a local grounding electrode (and didn't size a GEC).
I haven't personally inspected the other sites to know if the contractor knew to tie the transformer to a grounding electrode, but since no GEC was sized or called out in our drawing I would be surprised if they did. My question to everyone is am I correct in my current review that my transformer, a 5kVA 120V single phase secondary, is a separately derived system that requires a direct connection to a grounding electrode? I see that there is an exception for <1kVA transformers that is commonly used for control transformers, but I can't use that to justify no GEC for a 5kVA.
My second question is I thought that my EGC served dual purpose as an EGC connection, but after reviewing all of the previous topics I am not confident that this is a code compliant installation. The EGC run in the feeder for the control transformer is sized per table 250.66. Reading NEC 2014 250.121 makes me think that this isn't proper:
Chiefly, we aren't using Cadweld or permanent compression connections for the EGCs.
Tl;dr: Previous installations used the EGC as a GEC (sized per 250.66) but this isn't approved on a new site.
Final question/takeaway: Is there a summary of what exactly I would need to do to my EGC to use it as a GEC or is it just cheaper/easier to add a new GEC connection to a nearby grounding electrode?
EGC as GEC seems to be a hot topic that has been discussed in great depth already on this forum; unfortunately, I have not seen a definitive answer to my specific question so I thought I would spark a continued discussion now.
We use the same vendor for compressors on all of our sites and provide the same single line for each installation. The compressor MCC has a 5kVA 480/120V step down transformer to provide control power and 120VAC auxiliary power. Dozens of other sites have received inspector approvals, but this new site we're building is receiving push-back because we do not detail a connection back to a local grounding electrode (and didn't size a GEC).
I haven't personally inspected the other sites to know if the contractor knew to tie the transformer to a grounding electrode, but since no GEC was sized or called out in our drawing I would be surprised if they did. My question to everyone is am I correct in my current review that my transformer, a 5kVA 120V single phase secondary, is a separately derived system that requires a direct connection to a grounding electrode? I see that there is an exception for <1kVA transformers that is commonly used for control transformers, but I can't use that to justify no GEC for a 5kVA.
My second question is I thought that my EGC served dual purpose as an EGC connection, but after reviewing all of the previous topics I am not confident that this is a code compliant installation. The EGC run in the feeder for the control transformer is sized per table 250.66. Reading NEC 2014 250.121 makes me think that this isn't proper:
Code:
250.121 Use of Equipment Grounding Conductors. An
equipment grounding conductor shall not be used as a
grounding electrode conductor.
[I]Exception: A wire-type equipment grounding conductor installed[/I]
[I]in compliance with 250.6(A) and the applicable requirements[/I]
[I]for both the equipment grounding conductor[/I]
[I]and the grounding electrode conductor in Parts II, III, and[/I]
[I]VI of this article shall be permitted to serve as both an[/I]
[I]equipment grounding conductor and a grounding electrode[/I]
[I]conductor.[/I]
Chiefly, we aren't using Cadweld or permanent compression connections for the EGCs.
Tl;dr: Previous installations used the EGC as a GEC (sized per 250.66) but this isn't approved on a new site.
Final question/takeaway: Is there a summary of what exactly I would need to do to my EGC to use it as a GEC or is it just cheaper/easier to add a new GEC connection to a nearby grounding electrode?