Re: EGC color
Ok if you have installed bare grounding wires, where can you use a green conductor for anything else when it is prohibited in 400.23
400.23 Equipment Grounding Conductor Identification.
A conductor intended to be used as an equipment grounding conductor shall have a continuous identifying marker readily distinguishing it from the other conductor or conductors. Conductors having a continuous green color or a continuous green color with one or more yellow stripes shall not be used for other than equipment grounding purposes. The identifying marker shall consist of one of the methods in 400.23(A) or (B).
And the definition's (All Three) describe that the two are in fact are one, just differant locations!
Grounding Conductor. A conductor used to connect equipment or the grounded circuit of a wiring system to a grounding electrode or electrodes.
Grounding Conductor, Equipment. The conductor used to connect the non?current-carrying metal parts of equipment, raceways, and other enclosures to the system grounded conductor, the grounding electrode conductor , or both, at the service equipment or at the source of a separately derived system.
Grounding Electrode Conductor. The conductor used to connect the grounding electrode(s) to the equipment grounding conductor , to the grounded conductor, or to both, at the service, at each building or structure where supplied from a common service, or at the source of a separately derived system.
[ March 13, 2003, 11:43 PM: Message edited by: hurk27 ]