Is there a Rule-of-Thumb when deciding to use conduit or wire for an egc?
I seem to recall that the city of Chicago specifically requires a separate ground wire.
Thanks.
Well I'm asking because the project is an existing grounding system assessment. In all our new projects, we specify egc wire to be installed with feeders. If client wants to remain using the conduit as egc, they need to do testing on it, correct?
The same can certainly be said about a conductor-based EGC system.Although the conduits being used as egc are code compliant, I can't assure in my assessment that the conduit is installed in a correct way that it will provide a low-impedance path with only visual inspection and no testing.
The same can certainly be said about a conductor-based EGC system.
The same can certainly be said about a conductor-based EGC system.
I agree, and bad wirenut joint on a wire is just as like ly to come loosed under vibration than a setscrew.
A properly sized, properly installed pipe EGC, will IMO be a better fault current path than the same comparable wire EGC.
I would think that a ground wire comes in handy if the conduit breaks. You would have a continuous fault current path back to the service.
I agree! I see EGC un-spliced too often.In my experience the conductor most likely to be poorly spiced, or not spliced at all is the EGC.
So can we agree that for existing conditions, were conduit is used as EGC, is not worth it to pull the existing feeders out just to add a wire EGC? If installation is correctly done, conduit EGC is fine.?
But for new projects, Am I over-designing it by bonding the conduits and providing a wire EGC with all feeders and branch circuits?
Definitely not worth it, unless the customer wants to pay for it to be done. I wouldn't.So can we agree that for existing conditions, were conduit is used as EGC, is not worth it to pull the existing feeders out just to add a wire EGC?
Effectively grounded to mounting means is not an effective fault path per se - but does help - in most cases - hurt if isolated and energized. Someday ask me about the dishwashers who went on strike due to multiple faults at various equipment and WALLS..... Boy ....was that a fun job!On jobs that have steel structures, we will install metal conduit systems w/o any additional EGCs. The conduit is firmly fastened to the building steel with every strap, box, etc. A loose fitting won't make much difference in the event of a ground fault condition.