On a service upgrade, I ran the GEC from the rod to the new panel and landed it on the ground bus. The ground buss is naturally bonded to the neutralas this is the service disconnect.
Inspector says that this is a violation adn that I must move the gec to the neutral buss
I pointed out the #6 main bonding jumper from the nuetral buss to the ground buss to which she replies, ""The egc must land at the neutral bus. The fact that it is bonded to the ground buss is irrelevant."
OK electrically the two points are the same. Is she correct that the NEC requires the gec to land on the neutral buss even though it's bonded?
Thanks
Inspector says that this is a violation adn that I must move the gec to the neutral buss
I pointed out the #6 main bonding jumper from the nuetral buss to the ground buss to which she replies, ""The egc must land at the neutral bus. The fact that it is bonded to the ground buss is irrelevant."
OK electrically the two points are the same. Is she correct that the NEC requires the gec to land on the neutral buss even though it's bonded?