Hey all,
I'm trying to square the code in regards to fault current with what common sense and physics tells me:
Imagine an industrial circumstance (no general public access) where the service is 3ph 480 3wire with no neutral, nor a grounded leg. I don't currently know if this is the case, but this possibility was tossed out there by another party involved with the project in advance of seeing the site (state of California - CEC is based on NEC 2008).
Further suppose that equipment is tied to an EGC created by the bonded conduit back to the service (per 250.118), and there's a GEC and grounding electrode at the service, and they are connected to the egc per 250.24(D).
---
Since the secondary is not grounded, there is no fault current return path to the xfmr. Also, since the voltage is less than 600V, the grounding electrode is excluded from being the fault current path (250.4).
Practically this means that a fault to EGC only serves to raise the bond path GEC, and GE to phase voltage, and more than likely not tripping the overcurrent and clearing the fault, leaving an energized grounding path.
How does one square up this reality with the code's grounding, bonding, and fault current path requirements? Is there a specific section and/or exceptions in the code that allow for the operation of an ungrounded 3wire system of this type (beyond 250.20)?
P.S. If the current infrastructure turns out to be floating, it will have to remain so. There will be no opportunity for transition to grounded delta or use of a zig-zag ground.
Thanks in advance for any and all clarity!
I'm trying to square the code in regards to fault current with what common sense and physics tells me:
Imagine an industrial circumstance (no general public access) where the service is 3ph 480 3wire with no neutral, nor a grounded leg. I don't currently know if this is the case, but this possibility was tossed out there by another party involved with the project in advance of seeing the site (state of California - CEC is based on NEC 2008).
Further suppose that equipment is tied to an EGC created by the bonded conduit back to the service (per 250.118), and there's a GEC and grounding electrode at the service, and they are connected to the egc per 250.24(D).
---
Since the secondary is not grounded, there is no fault current return path to the xfmr. Also, since the voltage is less than 600V, the grounding electrode is excluded from being the fault current path (250.4).
Practically this means that a fault to EGC only serves to raise the bond path GEC, and GE to phase voltage, and more than likely not tripping the overcurrent and clearing the fault, leaving an energized grounding path.
How does one square up this reality with the code's grounding, bonding, and fault current path requirements? Is there a specific section and/or exceptions in the code that allow for the operation of an ungrounded 3wire system of this type (beyond 250.20)?
P.S. If the current infrastructure turns out to be floating, it will have to remain so. There will be no opportunity for transition to grounded delta or use of a zig-zag ground.
Thanks in advance for any and all clarity!