Unknown building supply / Commercial tenant space has 3 phase 4 wire 120/208 Y Sub-Panel.
Review of the circuits and grounding means for a new tenant showed 39 volts EGC to isolated NEUTRAL. Strange enough was the voltage test from circuits line 1, 2, or 3 showed a normal 120 volts to neutral, but when tested the circuits to EGC, the test showed 147 volts.
My first thought was a loose EGC at the distribution point allowing the EGC to pick up inductance outside of the tenant space.
My second thought was a fault on the EGC somewhere else in the building that is not "tripping"a breaker somewhere outside of the tenant space.
Would my thoughts seem accurate? Any other thoughts?