any short ahead of your OCP device (at the transformer can, in the supply to the OCP, etc) would require bonding to be sized per 250.66. Any falult ahead of the secondary has no OCP to trip so you would treat it just as you do a service.
In this situation, since you already have a ground bar connected to XO for your grounding electrode connection, IMHO, you need a 5th wire to the panel which would serve as the ahead of OCP bond for the panel, and the path for the EGC to return power to the source.
You know I think this IS right. It makes since and I remember this illustration from one of MH books showing the difference. It was a service disconnect but the idea is the same. Inside the disconnect the jumpers going from the MBJ to the raceways on the load side were sized to 250.122 and the jumpers going from the same point (MBJ) to the raceways on the line side were sized to 250.66.
Oh well. You think anyone on this site changes their mind as much as I do?
I like what MH says- have no loyalties to your opinions.