A similar situation/question.
The job calls for a #3 conductor on a 20A circuit. The engineer shows the correct size ground based on the proportional rule found in 250.122(B). The #3 was chosen to account for voltage drop.
The contractor wants to install #2 because of greater availability instead of the #3.
The 2014 NEC is clear about increasing the ground size but the 2014 NECHB commentary discusses this increase is needed based on "to compensate for voltage drop or for any other reason related to proper circuit operation" reasons. A "commercial" reason would not dictate an increased ground size...
The question is does the ground need to be adjusted again based on the contractors choice to install larger wire? Why or why not?