Re: EGC size
I got into this one late, but here's my contribution.
Last week, I heard a presentation from an expert who offered the following explanation for upsizing the EGC: No matter what reason led to you upsize the phase conductors, by doing so you have lowered the impedance of one half of the fault current path. From the source to the load (i.e., the hot-to-case fault point), the impedance will be lower. But that will not (he said) be enough. You need to reduce the impedance of the other half of the path (i.e., the EGC). Otherwise (again, he said), there will not be enough fault current to trip the OCPD.
I made a quick attempt to calculate one sample fault, and could not substantiate his statements. However, at least in the case of upsizing for voltage drop (i.e., for long runs), it makes sense to me that a larger EGC will reduce the impedance of the fault path, and result in a faster trip of the OCPD.