Re: EGC size
Here is Mike Holts authors comment in his 2002 Grounding & Bonding text on section 250.122(B)
"ungrounded circuit conductors could be increased in size to accomidate voltage drop, harmonic currents, fault currents, etc. For more information on sizing conductors for voltage drop see
www.mikeholt.com/studies/vd.htm"
However, more interesting is his comments following 250.122:
WARNING: Equipment grounding (bonding) conduc-
tors shall be capable of safely conducting any
ground-fault current likely to be imposed on them to ensure that the overcurrent protection device will quickly clear the ground fault [(250.4(A)5]. " the equipment grounding (bonding) conductor is not sized to withstand the ground-fault currents, the conductor may bum clear before the protective
device responds. For more information on this
subject,
http://www. NECcode.com/ Newsletters/7 -
21-99.htm.
---" AUTHOR'S COMMENT: A factor that must be
considered when sizing equipment grounding (bonding)
conductors is the terminal contact resistance. When an equipment bonding conductor carries fault current, the contact resistance of the conductor in the terminal might be less after the fault clears and the terminal cools. To
ensure proper conductor contact resistance, bonding conductors should be sized so that when they carry fault current, the temperature of the conductor and the terminal will not rise above 250?C (point at which cop-
per softens). To ensure that equipment grounding
(bonding) conductors can maintain proper contact
resistance, they should be sized so that their circular mil cross-sectional area is not smaller than the available ground-fault current1 times the following multiplier.
Protection Type Rating Multiplier
Breakers/Class H fuses -Opens
1/2 cycle 100A 1.56
Circuit breakers -Opens in 1 cycle 200A 1 .70
Circuit breakers -Opens in 2 cycle 400A 2.40
Circuit breakers -Opens in 3 cycle 1,200A 2.94
1 An Excel or Lotus spreadsheet to determine ground Fault current is available for free athttp://www.mikeholt.com/free/free.htm .