I know there is a thread somewhere concerning this but I can't find it.
Under 250.122(B), when one increases the CCC size because the COU derated ampacity of the original conductor choice is less than the next size down OCPD from the one on the circuit, does one have to increase the size of the EGC? I think not; it seems to me that the original choice does not meet "the minimum size that has sufficient ampacity for the intended installation", but whaddya think?
Under 250.122(B), when one increases the CCC size because the COU derated ampacity of the original conductor choice is less than the next size down OCPD from the one on the circuit, does one have to increase the size of the EGC? I think not; it seems to me that the original choice does not meet "the minimum size that has sufficient ampacity for the intended installation", but whaddya think?