I'm bidding on a job where the old RTU was a 3 phase 125amp rated unit. The new unit is 90 amp max fuse size. Because of length of run and old #1 Cu wires jammed in pipe its easier to leave old phase conductors. Unfortunately, the conduit was the egc but had to be removed below the gutter and some 1" Sealtight ran to make it to new disconnect area. I have a 2 part question.
Can I run old pipe into a 12x12 metal enclosure then out with sealtight to RTU ? (right above acoustical ceiling grid) provided I bond the enclosure ? Thinking yes
Can I run a # 4 Cu THWN (for the new egc) from a bonding lug in enclosure through sealtight to the new disconnect based on max 90 amp breaker? I know a # 4 Cu doesn't match the #1 cu in size but I was hoping the new load would trump this ?? The old 125 amp breaker would be replaced to a 90 amp as well at the disconnect on the roof.