How many of you bond your EGC to your 1900 boxes everytime you make a tap up in one? From what Ive read seems like if there is a tap to be made in the box it needs to be....
 

raider1

Senior Member
Staff member
Location
Logan, Utah
How many of you bond your EGC to your 1900 boxes everytime you make a tap up in one? From what Ive read seems like if there is a tap to be made in the box it needs to be....

I always bond the EGC to the 1900 box where it is spliced or terminated on a device.

Chris
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
Nothing to add, except I don't ground 4 squares when they're only used as a pull point. I do leave a loop in all the wires for future splicing though.:wink:
 