jwelectric said:
If the term equipment grounding is changed to equipment bonding then what will the equipment bonding conductor connect to in an ungrounded delta system?
Now if you say to the grounding electrode then it must be the equipment grounding conductor again.
That reasoning doesn?t hold up to further scrutiny. . The neutral is connected to the star just as completely as the equipment conductor. . Try to use that reasoning with the neutral and what happens ?
. . What does the grounded conductor connect to in a grounded delta system?
. . Now if you say to the grounding electrode then the grounded conductor must be called a ground
ing conductor.
And since that?s not true, you see that reasoning doesn?t work.
jwelectric said:
But if it is left the equipment grounding conductor and we keep the requirement to bond the electrode, enclosure and equipment grounding conductors at the service as it is now required then I can?t see any confusion.
I can?t see any confusion no matter how you look at it.
Just because there's a "star" point for bonding in the main disconnect doesn't mean that all of the wires that terminate there are all the same and/or do the same job/function.
1] Service neutral [or grounded phase for corner grounded delta]
2] Load neutral conductor or bar
will both continue to be current carrying or unbalanced current conductors even tho connected to the ?star?. . They remain ground
ed conductors even when connected to ground
ing conductors.
3] Electrode grounding/earthing conductor(s)
will continue to establish zero potential to earth and make the system invisible to lightning even tho it?s connected to other wires that are doing other jobs. . It remains a ground
ing conductor even when connected to ground
ed conductor(s).
4] Equipment grounding/bonding conductor, conduit, or bar
5] Service disconnect enclosure
will both continue to provide fault current path to operate OCPD. . They remain ground
ing even when connected to ground
ed conductor(s). . They continue to provide a grounding bonding function even when connected to a conductor that provides grounding earthing function.
The absence of a ground
ed conductor does not affect the ground
ing conductors requirements, either electrode earthing or equipment bonding.
David