wwhitney said:
If I understand Crossman's point, it is that the #12 wire is already connected to the box. That is via "box -- EMT -- panel case -- grounding bar -- #12 wire". So from that point of view, why is it necessary to add another connection within the box?
Yours, Wayne
Thanks, Wayne, I think I may have been missing a subtle
part of the argument.
I guess the argument is the definition of the word "to"
in 250.148. My interpretation is that the way the word
"to" is used is synonymous with "directly to". As
evidence of this interpretation, refer to the Exception
which states:
"... shall not be required to be connected to the other
EGCs or to the box."
If the definition of "to" included the path "through the
groundbar, panel, emt to the box" the word "or" (to the
box) would not be used because by that definition the
other EGCs would be connected to the box and the "or"
would be an "and." I believe the use of the word "to"
is used consistently this way in 250.148.
I think the above is a reasonable interpretation of what
250.148 states, and thus enforceable by the AHJ.