I don't see any language in 250.130(C) that restricts it to 120V receptacles.As I understand it, you could do that for a two wire 120V receptacle, but not for a high current 240V range receptacle.
But 240 is much more likely to be more than two poles in the first place.I don't see any language in 250.130(C) that restricts it to 120V receptacles.
Cheers, Wayne
Yes, you can.If I have a range receptacle installed 1960 with 3 wires I can not install a EGC on the outside of the cable to make it a 4 wire receptacle ? per code. ( not that I want to or would. just trying to understand this article .
250.130 (2011) doesn't use the word "two", as in two-wire. Is there a different section that refers to that? The last sentence of 250.130 says "For replacement of non–grounding-type receptacles with grounding-type receptacles and for branch circuit extensions only in existing installations that do not have an equipment grounding conductor in the branch circuit, connections shall be permitted as indicated in 250.130(C).But 240 is much more likely to be more than two poles in the first place.
It does not say you can do this for any ungrounded receptacle can be treated this way, only a two wire.
Yes, you can.
Glad you agree. One thing I'm having trouble with. You list your location as Texas. I'm a Coloradan. Please tell me you moved there from somewhere else.I concur because 250.130(c) is referencing non-grounding type receptacles and circuits w/ no egc, and those 3wire range circuits and old NEMA 10-30 and 10-50 tombstones were just that.
Glad you agree. One thing I'm having trouble with. You list your location as Texas. I'm a Coloradan. Please tell me you moved there from somewhere else.
I moved to Texas from Louisiana, but I moved to Austin, which isn't a whole lot like the rest of Texas.Glad you agree. One thing I'm having trouble with. You list your location as Texas. I'm a Coloradan. Please tell me you moved there from somewhere else.
You can't run it on the outside of conduit.If you were to run the EGC on the on the outside of the cable or conduit how would you terminate the EGC to the panel . if you use thhn wire ?
You can't run it on the outside of conduit.
He could if it were bare copper, couldn't he?You can't run it on the outside of conduit.
You're doing my head in mate.YES you can.
No. 250.102 is the only place where it is allowed. That section deals with bonding jumpers and restricts the length to six feet, except for grounding electrode connections.He could if it were bare copper, couldn't he?
YES you can.