3P-1N-1G in each set. 24 sets.You could use the raceway as an EGC. How many conductor sets are in this feeder?
Your EGC in each set is is much too small. In fact with 250.122(B) and up sizing for 24 sets using a wire type EGC is not practicable.3P-1N-1G in each set. 24 sets.
But what about "A" that says "in no case shall they be required to be larger than the circuit conductors supplying the equipment"?Your EGC in each set is is much too small. In fact with 250.122(B) and up sizing for 24 sets using a wire type EGC is not practicable.
The circuit conductors are 24 parallel sets of 600 kcmil or 14400 kcmil not 600 kcmil.But what about "A" that says "in no case shall they be required to be larger than the circuit conductors supplying the equipment"?
Upsizing? Why and where?Your EGC in each set is is much too small. In fact with 250.122(B) and up sizing for 24 sets using a wire type EGC is not practicable.
Huh???The circuit conductors are 24 parallel sets of 600 kcmil or 14400 kcmil not 600 kcmil.
Yes. You need to calculate the upsizing of the ungrounded conductors from 10 sets of 600's to 24 sets to size the EGC.Huh???14400cmil? Why do you multiply the sets x the conductor size?
The code section is right there in post #5.Upsizing? Why and where?
The table says #500 EGC for 4000A OCPD.
So the increase in size section, got it.The code section is right there in post #5.
600*10=6000 kcmil increased to 600*24=14400 kcmil. That's a factor of 2.4. 500 kcmil*2.4=1250 kcmilSo the increase in size section, got it.
So the ungrounded conductors have obviously been increased.
Now the wire type EGC must be increased in size proportionally.
That's the math I don't follow?
BTW, it does say increased in size. The # of sets are really increased not the size. ??
I'm not sure I agree with your interpretation. It says the ground wire doesn't have to be any larger than the circuit conductors. A conductor is a conductor, not the equivalent size of a group of parallel conductors.The circuit conductors are 24 parallel sets of 600 kcmil or 14400 kcmil not 600 kcmil.
The interpretation is correct. If you had 10 sets of #3/0 for a 2000 amp feeder the minimum size EGC is 250 kcmil. You cannot use a #3/0 EGC just because you chose #3/0 as the ungrounded conductor size.I'm not sure I agree with your interpretation. It says the ground wire doesn't have to be any larger than the circuit conductors. A conductor is a conductor, not the equivalent size of a group of parallel conductors
700' run, he said for voltage drop compensation.Clarify.... The are calling for 24 sets of 600CU on a 4000 amp feeder ??
Any idea why ?
Or a 4160 feeder.Talk about a good place for POCO primary.
The interpretation is correct. If you had 10 sets of #3/0 for a 2000 amp feeder the minimum size EGC is 250 kcmil. You cannot use a #3/0 EGC just because you chose #3/0 as the ungrounded conductor size.