Unfortunately the OP is under the 2008 NEC.If your on the 2020 NEC there is an exception. Para phrase: Size by a qualified person. See 2020 NEC for complete wording as the rest of what it says is important.
OP profile says New Jersey, which adopted the 2000 NFPA-70 on 9/6/2022Unfortunately the OP is under the 2008 NEC.
That exception requires a qualified PE licence under engineering supervision, with questionable benefit.If your on the 2020 NEC there is an exception. Para phrase: Size by a qualified person
Did not see that stated here, but #600 would work, even with 310.15(B)(5)(c) counting 4 ccc's700' run, he said for voltage drop compensation.
600*10=6000 kcmil increased to 600*24=14400 kcmil
This would be a good subject to get a 100% definitive answer to which is correct.Well, right about 6 min and 30 sec, Mike says the equipment grounding conductor doesn't have to be larger than the phase conductor. But right about the end, someone else says the grounding conductor may have to be large than the phase conductors, then there seems to be some discussion about what actually got put in the code right as the video ends.
So I don't think its cut and dry by any means. To me it says what it says, and it says it doesn't have to be larger than the phase conductors "in any case".
https://www.bing.com/videos/search?q=NEC+250.122+EXAMPLES+FOR+PARALLEL+CONDUITS&qs=n&=Search+{0}+for+{1},Search+work+for+{0},%eManage+Your+Search+History%E&sp=-1&pq=nec+250.122+examples+for+parallel+conduits&sc=9-42&sk=&cvid=C38F996E0ADC4F9BB82F923F74D94D86&ghsh=0&ghacc=0&ghpl=&sid=04B9DCF2E0FC6EC103E2CE88E12F6F98&jsoncbid=1&ru=/search?q=NEC%20250.122%20EXAMPLES%20FOR%20PARALLEL%20CONDUITS&qs=n&form=QBRE&=Search%20%7B0%7D%20for%20%7B1%7D&=Search%20work%20for%20%7B0%7D&=%25eManage%20Your%20Search%20History%25E&sp=-1&pq=nec%20250.122%20examples%20for%20parallel%20conduits&sc=9-42&sk=&cvid=C38F996E0ADC4F9BB82F923F74D94D86&ghsh=0&ghacc=0&ghpl=&sid=04B9DCF2E0FC6EC103E2CE88E12F6F98&format=snrjson&jsoncbid=1&view=detail&mmscn=vwrc&mid=B91CDEBC7529AE1AEE13B91CDEBC7529AE1AEE13&FORM=WRVORC
CMP-5's opinion is that the phase conductor for parallel sets is the sum of the areas of all of the conductors that are connected in parallel, so the EGC for a single set of parallel conductors may be larger than the ungrounded conductors in each raceway.Well, right about 6 min and 30 sec, Mike says the equipment grounding conductor doesn't have to be larger than the phase conductor. But right about the end, someone else says the grounding conductor may have to be large than the phase conductors, then there seems to be some discussion about what actually got put in the code right as the video ends.
So I don't think its cut and dry by any means. To me it says what it says, and it says it doesn't have to be larger than the phase conductors "in any case".
https://www.bing.com/videos/search?q=NEC+250.122+EXAMPLES+FOR+PARALLEL+CONDUITS&qs=n&=Search+{0}+for+{1},Search+work+for+{0},%eManage+Your+Search+History%E&sp=-1&pq=nec+250.122+examples+for+parallel+conduits&sc=9-42&sk=&cvid=C38F996E0ADC4F9BB82F923F74D94D86&ghsh=0&ghacc=0&ghpl=&sid=04B9DCF2E0FC6EC103E2CE88E12F6F98&jsoncbid=1&ru=/search?q=NEC%20250.122%20EXAMPLES%20FOR%20PARALLEL%20CONDUITS&qs=n&form=QBRE&=Search%20%7B0%7D%20for%20%7B1%7D&=Search%20work%20for%20%7B0%7D&=%25eManage%20Your%20Search%20History%25E&sp=-1&pq=nec%20250.122%20examples%20for%20parallel%20conduits&sc=9-42&sk=&cvid=C38F996E0ADC4F9BB82F923F74D94D86&ghsh=0&ghacc=0&ghpl=&sid=04B9DCF2E0FC6EC103E2CE88E12F6F98&format=snrjson&jsoncbid=1&view=detail&mmscn=vwrc&mid=B91CDEBC7529AE1AEE13B91CDEBC7529AE1AEE13&FORM=WRVORC
The exception only says "qualified person" and does not say engineering supervision. This becomes a judgement call on the part of the AHJ. There are a number of electrical engineering software programs out there that can do this calculation and there is no need for a PE to input numbers into a software program.OP profile says New Jersey, which adopted the 2000 NFPA-70 on 9/6/2022
That exception requires a qualified PE licence under engineering supervision, with questionable benefit.
However, same 2020 NEC changes remove upsizing EGC for any reason except voltage drop.
Did not see that stated here, but #600 would work, even with 310.15(B)(5)(c) counting 4 ccc's
I like horsegoer's original idea to submit an RFI for using metallic raceway for EGC, per 250.96-102. Even though 2/0 bonding jumpers might get ugly.
I agree. I have seen feeders with EGC's larger than the ungrounded conductors.CMP-5's opinion is that the phase conductor for parallel sets is the sum of the areas of all of the conductors that are connected in parallel, so the EGC for a single set of parallel conductors may be larger than the ungrounded conductors in each raceway.
And it usually will happen once you get past 3 or 4 parallel sets in the run.I agree. I have seen feeders with EGC's larger than the ungrounded conductors.
I'm not seeing that prohibition in 2017, 2020, or 2023.3 sets of 500 kcmil in parallel is effectively 1500 kcmil. There is no allowance for paralleling EGC's to effectively make a larger conductor, or wasn't before 2020 NEC anyway that I have ever been aware of.
Yet if those conductors were transformer secondary conductors, I would install a supply side bonding jumper in each raceway sized per Table 250.102(C)(1) and would have a 1/0 SSBJ in each raceway. For any place you use a supply side bonding jumper, you would never have the bonding jumper larger than the ungrounded conductors in any raceway.And it usually will happen once you get past 3 or 4 parallel sets in the run.
3 sets of 500 kcmil in parallel is effectively 1500 kcmil. There is no allowance for paralleling EGC's to effectively make a larger conductor, or wasn't before 2020 NEC anyway that I have ever been aware of.
At same time OP would be compliant to use the metal raceway as the EGC, and will save just a little copper doing so.
regardless of what code might say I agree it makes no sense to require a grounding or bonding conductor larger then the largest ungrounded conductor in a raceway.Yet if those conductors were transformer secondary conductors, I would install a supply side bonding jumper in each raceway sized per Table 250.102(C)(1) and would have a 1/0 SSBJ in each raceway. For any place you use a supply side bonding jumper, you would never have the bonding jumper larger than the ungrounded conductors in any raceway.
Why is that? If the parallel conductors are #1/0 and the required EGC is 250 kcmil then it would be okay to undersize the EGC.and use a #1/0?regardless of what code might say I agree it makes no sense to require a grounding or bonding conductor larger then the largest ungrounded conductor in a raceway.
If the sets are in separate raceways why not? A fault in the raceway is not carrying any more current than the 1/0 ungrounded conductor can deliver. If the paralleled 1/0 are all in the same raceway then I believe the 250 EGC would be needed.Why is that? If the parallel conductors are #1/0 and the required EGC is 250 kcmil then it would be okay to undersize the EGC.and use a #1/0?
But it is. The fault is being feed from both ends of that 1/0 because of its parallel connection to the rest of that phase.If the sets are in separate raceways why not? A fault in the raceway is not carrying any more current than the 1/0 ungrounded conductor can deliver. If the paralleled 1/0 are all in the same raceway then I believe the 250 EGC would be needed.
From what we have discussed here many times, a correctly-assembled EMT system has better fault-current performance than the EGC that would otherwise accompany the conductors the EMT could contain.As far as the EMT as the EGC. I will review my book on the use of EMT and it foot limitation as an effective ground fault path.
In my opinion, yes because that is still larger than what would be required for a supply side bonding jumper with parallel sets of conductors.Why is that? If the parallel conductors are #1/0 and the required EGC is 250 kcmil then it would be okay to undersize the EGC.and use a #1/0?
In the case of the EGC it's required to be larger than the ungrounded parallel conductors when situations like the one in this thread is encountered. I agree with you that when using a SSBJ the conductor is typically smaller than the a similarly required EGC which makes no sense. Until the NEC comes up with a better rule for EGC's we're stuck with what we have.In my opinion, yes because that is still larger than what would be required for a supply side bonding jumper with parallel sets of conductors.
If you had parallel 1/0s in separate raceways where a supply side bonding jumper is used and not an EGC, the supply side bonding jumper would only be 6 AWG in each raceway. It is my opinion that locations where supply side bonding jumpers are used are a worse case as far as fault clearing as compared to where EGCs are used.
Thank you for letting me know.From what we have discussed here many times, a correctly-assembled EMT system has better fault-current performance than the EGC that would otherwise accompany the conductors the EMT could contain.