must i use grounding jumper from the rec, to the metal box, all conduit 2020 nec. ??????????????????????????????????????????????????????????????
must i use a egc wire in conduit or can i use the conduit as a EGC.With a metal box the EGC (if used) must be connected to the box. If you use a self-grounding receptacle a bonding jumper is not required. There are some other exceptions for different types of metal boxes and covers.
A wire type EGC is not required when the raceway qualifies as an EGC {250.118}must i use a egc wire in conduit or can i use the conduit as a EGC.