A "terminal bar" used for the termination of equipment grounding conductors is shown here on the right side of this cabinet.
This cabinet encloses a panelboard, and is usually called a "subpanel," and the panelboard's grounded conductor (neutral concuctor, with the white identification) is "isolated" or "floating from the metal cabinet, or so called "can" and the EGC terminal is "BONDED" to the can.
This is a "terminal bar" and this is where the EGC's are to be secured under each terminal, some of which may only allow two of the same size per terminal.
The panelboard cover will include this information.
QUESTION: Are EGC's allowed to be spliced and "pigtailed" as shown below?
Here's a good example of what not to do in any panelboard, or approve when it comes to the equipment grounding conductors that are terminated in any type of cabinet:
http://joetedesco.com/nec/photos/twist1.jpg
The rule in 384-20, or now 408.20 was added to the code a long time ago to put a stop to this method.
In addition, the NEC 1989 TCR, on Page 352 for Proposal 9-142, Section 384-27, Log #1039 was "Accepted in Principle" and included in the substantiation were the following words:
"The second sentence is changed to eliminate superfluous wording"
The committee also changed the Section number from 384-27 to 384-20.
NECH 408.20 Commentary:
Courtesy: www.nfpa.org
[ July 29, 2003, 05:09 AM: Message edited by: joe tedesco ]
A "terminal bar" used for the termination of equipment grounding conductors is shown here on the right side of this cabinet.
This cabinet encloses a panelboard, and is usually called a "subpanel," and the panelboard's grounded conductor (neutral concuctor, with the white identification) is "isolated" or "floating from the metal cabinet, or so called "can" and the EGC terminal is "BONDED" to the can.
This is a "terminal bar" and this is where the EGC's are to be secured under each terminal, some of which may only allow two of the same size per terminal.
The panelboard cover will include this information.
QUESTION: Are EGC's allowed to be spliced and "pigtailed" as shown below?
Here's a good example of what not to do in any panelboard, or approve when it comes to the equipment grounding conductors that are terminated in any type of cabinet:
http://joetedesco.com/nec/photos/twist1.jpg
The rule in 384-20, or now 408.20 was added to the code a long time ago to put a stop to this method.
In addition, the NEC 1989 TCR, on Page 352 for Proposal 9-142, Section 384-27, Log #1039 was "Accepted in Principle" and included in the substantiation were the following words:
"The second sentence is changed to eliminate superfluous wording"
The committee also changed the Section number from 384-27 to 384-20.
NECH 408.20 Commentary:
Courtesy: www.nfpa.org
Photos: www.joetedesco.comA separate equipment grounding conductor terminal bar must be installed and bonded to the panelboard for the termination of feeder and branch-circuit equipment grounding conductors.
Where installed within service equipment, this terminal is bonded to the neutral terminal bar. Any other connection between the equipment grounding terminal bar and the neutral bar, other than allowed in 250.32, is not permitted.
If this downstream connection occurs, current flow in the neutral or grounded conductor would take parallel paths through the equipment grounding conductors (the raceway, the building structure, or earth, for example) back to the service equipment.
Normal load currents flowing on the equipment grounding conductors could create a shock hazard. Exposed metal parts of equipment could have a potential difference of several volts created by the load current on the grounding conductors.
Another safety hazard created by this effect, where subpanels are used, is arcing or loose connections at connectors and raceway fittings, for example, creating a potential fire hazard.