EGCs missing ?

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Client has a delta-delta ungrounded transformer (13.8kV to 480V, 2.0MVA), that feeds a 480V SWGR, 3P,3W, via bus duct to the XMFR secondary.
From the SWGR they feed 5, 480V MCCs,3P, 3W with parallel 500kCMIL conductors, BUT they do not show an EGC with any of the feeders…
As far as I know, you must have an EGC in each conduit for parallel feeders even if the upstream transformer is ungrounded. Am I missing something?