I am looking for specific code references showing the following installation requires a second means of egress. I believe Article 110.26 C(2) does not cover this particular installation as equipment is less than 1200A each.
I have an elevated platform approx 14' x 25' with One set of stairs and a ladder along east end of platform.
Mounted on the platform I have three Hazardous area 600A Outdoor Switchracks (Front/back arragement with starters and circuit breakers on each side) each about 20' long that extend from East end of platform to West end of platform. One of the switchracks ends at the west end of the platform without the ability to walk around equipment (Due to proximity to handrail).
I am argueing for a 2nd means of egress from platform, (From a common sense and safety standpoint) but can not find the code references to support my argument.
I have an elevated platform approx 14' x 25' with One set of stairs and a ladder along east end of platform.
Mounted on the platform I have three Hazardous area 600A Outdoor Switchracks (Front/back arragement with starters and circuit breakers on each side) each about 20' long that extend from East end of platform to West end of platform. One of the switchracks ends at the west end of the platform without the ability to walk around equipment (Due to proximity to handrail).