When installing emergency lighting in a warehouse, manufacturing facility or other high bay lighting area, we typically use modular wiring reloc or similar and either a lighting relay panel or multiple lighting contactors for control of the lighting in the high bay area.
For egress lighting, we typically use battery packs/bug eyes/unit equipment and run a separate MC cable to power these fixtures as well as the exit signs and remote heads.
We also have installed similar fixtures with on board occupancy sensors where the fixture circuit is connected directly to the panel since the controls are on board the fixture.
My question is can we use the modular wiring to supply the normal lighting AND the egress lighting(ie. unit equipment, exits, etc.) in the same cable fed from the same breaker as long as the egress lighting is understood to be connected ahead of any switching device?
In the instance of the contactor or relay panel, I am proposing that we could install a 12/3 branch circuit to supply the and 1-phase conductor would be for the switched normal lighting loads(same ckt as egress), and the other phase conductor would be a constant hot from the panel for the unswitched egress lighting loads(same ckt as normal). The switched and unswitched conductors would share the same neutral in the same cable.
In the instance of the on board occupancy sensor, I am proposing that we could install a 12/2 branch circuit and the phase conductor would be a constant unswitched hot from the panel that would supply power both the the fixtures with occupancy sensors and the egress lighting loads.
We've gone back and forth with this internally and wanted to throw the question out to see if anyone has come across a similar instance.
Reference Code Articles 700.12(F),700.12(F)(3), 700.12(F)(4), 700.19
For egress lighting, we typically use battery packs/bug eyes/unit equipment and run a separate MC cable to power these fixtures as well as the exit signs and remote heads.
We also have installed similar fixtures with on board occupancy sensors where the fixture circuit is connected directly to the panel since the controls are on board the fixture.
My question is can we use the modular wiring to supply the normal lighting AND the egress lighting(ie. unit equipment, exits, etc.) in the same cable fed from the same breaker as long as the egress lighting is understood to be connected ahead of any switching device?
In the instance of the contactor or relay panel, I am proposing that we could install a 12/3 branch circuit to supply the and 1-phase conductor would be for the switched normal lighting loads(same ckt as egress), and the other phase conductor would be a constant hot from the panel for the unswitched egress lighting loads(same ckt as normal). The switched and unswitched conductors would share the same neutral in the same cable.
In the instance of the on board occupancy sensor, I am proposing that we could install a 12/2 branch circuit and the phase conductor would be a constant unswitched hot from the panel that would supply power both the the fixtures with occupancy sensors and the egress lighting loads.
We've gone back and forth with this internally and wanted to throw the question out to see if anyone has come across a similar instance.
Reference Code Articles 700.12(F),700.12(F)(3), 700.12(F)(4), 700.19