I want to run a circuit for an exterior sign 16' above the interior stairwell landing in a hospital, the mid landing between the top floor and the roof. Does the IBC permit this?
How many stories is your hospital?
I am not sure if building code allows for this. Why wouldn't building code permit it? Maybe needing to be fircaulked? As long as it wouldn't imped the flow of foot traffic. Or reduce the lumens below the permissible level in the stairway. I couldn't tell you the answer, but I can't see why not.
Im here to learn
Five.
You're not a high rise but you still have 1009.3.1.5 and 1009.3.1.5.1 which says it's a no go.
If that's a 2 hour stairwell and you can put a 2 hour barrier around it, the code authorities may see that as being outside of the stairwell because it and the stairwell will be separated by the required rating of the stairwell. You should run this by the bldg dept, the fire marshal and the state agency for healthcare admin if you want to try this route.
I want to run a circuit for an exterior sign 16' above the interior stairwell landing in a hospital, the mid landing between the top floor and the roof. Does the IBC permit this?
In NJ it's the Joint Commission, and they frequently have more stringent requirements than the building/fire code.
The joint commission isn't an AHJ or a code enforcement agency. They are an accreditation and certification agency. At least around here.
Sure, most hospitals' want a good review from them, but I don't think they are likely to be looking something like this.
You would be amazed. At my last company we had a number of health care facilities as clients, all under the jurisdiction of the Joint Commission. It didn't matter if it met code, if it didn't meet the Joint Commission standards it was a deficiency, and they could shut down the facility for it.
In NJ it's the Joint Commission, and they frequently have more stringent requirements than the building/fire code.
In NJ it would be the Department of Community Affairs Bureau of Construction Project Review. They are responsible for all plan review for facilities that need licensing from the Department of Health and Human Services. They can release the review to the local building department if they feel the project warrants it.
You would be amazed. At my last company we had a number of health care facilities as clients, all under the jurisdiction of the Joint Commission. It didn't matter if it met code, if it didn't meet the Joint Commission standards it was a deficiency, and they could shut down the facility for it.
But Medicare and private insurance companies may not pay for treatment in unaccredited facilities.Q: Is accreditation or certification mandatory?
A: No. Health care organizations, programs, and services voluntarily pursue accreditation and certification.