And a PVC plumbing elbow has an even tighter radius, with a "compact" elbow being tighter still.
Funny you should mention that since I worked on a project in my fair city where some plumbing elbows were used in a sub-division. Pavement and side walks got dug up on several blocks before the problem 90's were discovered.
 
Bigger than what?? 36"?


Sent from my iPad using Tapatalk

Larger than what is shown in Chapter 9, Table 2.

While the assumption is that the use of the larger radius bends reduces the required pulling force, none of the cable calculation formulas I have seen show that. The use of the larger radius does reduce the sidewall pressure that can damage the conductor insulation. On most pulls with bends the sidewall pressure and not the pulling tension is the limiting factor for the pull.
 
What determine when you would use a large sweep/radius elbow?
The job design specs, or a pulling calculation that shows too much sidewall pressure with a standard radius elbow. Sidewall pressure is the crushing force between the conductor and the inside radius of the elbow when you are pulling the conductors. It is a function of the pulling tension and the radius of the elbow.
 