Assuming from the reference to 208V 3 phase that you are in North America. An ELCB would not have any valid installation acceptability here, it is a term for a form of ground fault protection in the IEC world, and an old one at that (they are now called RCDs). Here in NA, if you are wanting to protect people it must be a GFCI, which has a MUCH lower thrip threshold than an ELCB/RCD. The trip levels for an ELCB/RCD would qualify only as “equipment” ground fault protection, what we refer to as “GFPE”. If that’s what you need, get a UL listed circuit breaker with GFPE and a short circuit interrupting capacity commensurate with your installation.
I suspect that you got some piece of equipment in from Europe or Asia and their instructions call for this. That may be indicative of this not really being intended to be installed here, so compatibility with other aspects of our electrical systems should be looked at carefully as well.