Electric baseboard heaters

Status
Not open for further replies.

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
When all three heaters are on, the load will be balanced and you will have 12.5A/phase.

When only some of the heaters are on, the load will no longer be balanced, but you will still have less than 12.5A per phase.

Say the heater connected between A and B is on, and the B:C heater is on, but the A:C heater is off. You will have 12.5A on the B leg, and 7.2A on the A and C legs.

-Jon
 